% reactance of alternator on base kVA,
% reactance of transformer on base kVA,
% reactance of transmission line is
% age resistance of transmission line,
(i) Total % reactance = %X_A+%X_T+%XL
= 10 + 10 + 40 = 60%
% resistance = 10%
∴ % impedance from generator neutral upto fault point F2
= 60.83%
∴ Short-circuit kVA
(ii) For a fault at the high voltage terminals of the transformer (point F1),
Total % reactance from generator neutral upto fault point F1
∴ Short-circuit kVA
= 50000kVA
Related Question
View AllSmart Grid: A Smart Grid is an advanced electrical network that integrates traditional power infrastructure with modern Information and Communication Technology (ICT). Unlike traditional grids, it enables two-way flow of both electricity and data, allowing for real-time monitoring, automated control, and increased efficiency.